Are the efficiency tables totally wrong or is my math broken.
THE EFFECTS OF EFFICIENCY table shows some weird figures
So if we have a efficiency of 80% and draw of 400 the actual loss in power is 400*0.2 = 80W or 400* 1.2 - 400 ..
in that table the figure is 100W
So how am I calculating wrong?
For example, a power supply that requires 100W AC input to produce 70W DC output has an efficiency of 70%. In this example, 30W is lost as heat within the PSU.
Powersupply fundamentals and broken math ?
Moderators: NeilBlanchard, Ralf Hutter, sthayashi, Lawrence Lee, Edward Ng
-
- Posts: 2198
- Joined: Thu Feb 10, 2005 11:20 am
- Location: TN, USA
The correct math is (DC output / power from wall) = % efficiency but the table doesn't tell us power from the wall.
To find power from the wall we get (DC output / % efficiency) = Power from wall.
To find waste heat we have (Power from wall - DC output) = watts wasted.
Now if we use 100 W DC output / 80% efficiency it equals 125W. 125W - 100W = 25 watts wasted not the 20W you might have though of. The key is that you have to divide by efficiency in this case not multiply.
So the table in the article is most likely correct. We at least know that the 25W number in the intersection of 100W and 80% is correct.
If we use 400 W DC output / 65% efficiency it equals 615.38461538461538461538461538462W.
615W - 400W = 215W watts wasted, the table rounded up to 216W but maybe he used data for efficiency with more decimal places or maybe he just prefers to round up.
To find power from the wall we get (DC output / % efficiency) = Power from wall.
To find waste heat we have (Power from wall - DC output) = watts wasted.
Now if we use 100 W DC output / 80% efficiency it equals 125W. 125W - 100W = 25 watts wasted not the 20W you might have though of. The key is that you have to divide by efficiency in this case not multiply.
So the table in the article is most likely correct. We at least know that the 25W number in the intersection of 100W and 80% is correct.
Code: Select all
THE EFFECTS OF EFFICIENCY
Efficiency Power Lost as Heat
@100W output @200W output @400W output
85% 18W 35W 70W
80% 25W 50W 100W
75% 33W 67W 133W
70% 43W 86W 174W
65% 54W 108W 216W
615W - 400W = 215W watts wasted, the table rounded up to 216W but maybe he used data for efficiency with more decimal places or maybe he just prefers to round up.